Programmable indoor transmitter of temperature T0318, T0418
|
|
- Lizbeth Christiana Phillips
- 5 years ago
- Views:
Transcription
1 Programmable indoor transmitter of temperature T0318, T0418 Programmable indoor transmitter of temperature, relative humidity and other derived humidity values T3318, T3418 Programmable indoor transmitter of atmospheric pressure, temperature, relative humidity and other derived humidity values T7318, T7418 with RS232 / RS485 serial output Instruction Manual
2 Device type Instruction Manual Temperature Humidity Pressure Computed values Output Galvanic isolated output T RS232 - T RS485 T RS232 - T RS485 T7318 RS232 - T7418 RS485 Devices are designed for indoor applications. By device type (see previous table) they can measure ambient temperature at C or F, relative humidity of air without aggressive ingredients or atmospheric pressure. Measured temperature and relative humidity are recomputed to humidity expression: dew point temperature, absolute humidity, specific humidity, mixing ratio and specific enthalpy. Devices T7318 and T7418 support atmospheric pressure measurement at hpa, PSI, inhg, mbar, oz/in 2, mmhg, inh 2 O or kpa. They support pressure correction for altitude setting (offset). Unit choice is provided by User s software see later. Devices T0318, T3318 and T7318 communicate via link RS232, devices T0418, T3418 and T7418 via link RS485. Supported communication protocols are Modbus RTU, protocol compatible with standard Advantech-ADAM, ARION and communication with HWg Poseidon devices. Devices are preset from manufacturer to Modbus RTU communication protocol. If you would like to use different communication protocol then Modbus RTU, it is necessary preset them throw user s software see latter. Temperature, relative humidity eventually pressure sensors are non-removable device parts, pressure sensor is placed inside the electronic case. Measured and computed values are optionally shown on dual line LCD display. If there are two values displayed at one LCD line, they are periodically switched between both readings with period of 4 seconds. Display can be switched OFF totally too. Please read instruction manual before the first device connection. Use user s software Tsensor for setting of all device parameters (recommended). It is free to download at It supports make the adjustment of the device too. This procedure is described at file Calibration manual.pdf which is installed commonly with the software. Change of some parameters is possible to do without user s software with Windows hyperterminal (change of communication protocol, its parameters, LCD display setting). It is described in file Description of communication protocols of Txxxx series which is free to download at the same address. Device setting from the manufacturer If special setting was not required in the order device is set from the manufacturer to the following parameters: communication protocol: Modbus RTU device address: 01 communication speed: 9600Bd, without parity, 2 stop bits display: switched ON value displayed at higher line: temperature (temperature / pressure) by device type value displayed at lower line: relative humidity only by device type temperature unit: C pressure unit: hpa correction for altitude: 0 hpa(absolute pressure) preset computed value: dew point temperature 2 IE-SNC-TX3(4)18-06
3 Device installation Devices are designed for indoor applications. It is recommended to mount them on universal wiring box (common installation box KU68) with using two enclosed mounting screws. For correct function there is necessary to find proper device place. It shouldn t be placed at places where it can be affected by sunshine, near radiators, heating elements and other heat sources, air handlers, windows, doors, into racks and shelves and similar places. For buildings with less thermal insulation there is not suitable to place them on external walls of building. If there are communication conductors placed into conduit, there is strongly recommended make it caulk, to restrict air flow around device. Connect cables to terminals with respecting the signal polarity (see figure). Terminals are self-clamping and can be opened by a suitable screwdriver. For the opening, insert the screwdriver to upper terminal hole and lever by him. There are two ways, how to power devices with RS232 interface. They can be powered either from master device or from external power source. For powering from master device RS232 interface there is necessary to interconnect DTR and RTS signals with the device. For powering from external power source, there is necessary to connect positive power terminal to DTR into device terminal only and then do NOT interconnect DTR and RTS with master device. Devices with RS232 interface: Terminal Connect to ( female connector CANNON 9 termination ) GND Shielding, power source ground (PIN 5) Tx Output data for master device, transmit (PIN 2) Rx Input data from master device, receive (PIN 3) RTS DTR Connect with RTS signal to master device (PIN 7), eventually o not connect Connect with DTR signal to master device (PIN 4) or connect positive power terminal from external power source Devices with RS485 interface contain doubled connection terminals to provide continuous connection of next RS485 devices. Terminals description: Terminal A+, B- +U, GND Connect to RS485 communication line Shielding of communication line Power source positive terminal, power source ground For devices with RS485 interface here is recommended to use shielded twisted copper cable (e.g. SYKFY), maximal length 1200m. The cable must be located at indoor rooms. Nominal cable impedance should be 100 Ω, loop resistance max. 240 Ω, cable capacity max. 65 pf/m. Suitable cable is e.g. SYKFY 2x2x0.5 mm 2, where one wire pair serves for the device powering and the other pair for communication link. The cable should be led in one line, i.e. NOT to tree or star. Termination resistor should be located at the end. For short distance other topology is allowed. Terminate the network by a termination resistor. The value of the resistor is recommended about 120 Ω. For short distance termination resistor can be left out. The cable should not be led in parallel along power cabling. Safety distance is up to 0.5 m, otherwise undesirable induction of interference signals can appear. The same for devices with RS232 interface, but a maximal length is restricted to 15 m and allow connect only one device. Electrical system (wiring) may do only worker with required qualification by rules in operation. IE-SNC-TX3(4)
4 Dimensions T0418, T3418, T7418 RS485 T0318, T3318, T7318 RS232 4 IE-SNC-TX3(4)18-06
5 Device mounting Firstly mount back part of device onto wiring box with two holding screws. Connect cables to terminals with respecting the signal polarity (see figure). Terminals are self-clamping and can be opened by a suitable screwdriver. For the opening, insert the screwdriver to upper terminal hole and lever by him. Then insert front part of device firstly at bottom into hinge and then press both parts together see figure1 Figure1: Device mounting Device demounting If there is necessary demount the device, insert flat bladed screwdriver max. 3.5 mm wide from top side into middle device s air hole. There is fastening member placed, insert screwdriver beyond the fastening member about 2 cm deep number at the picture. Then slightly move screwdriver in arrow direction as shown at the picture. It unlock fastening member and the device is partially opened. Remove the screwdriver and take front part of device at top, see number at the picture. Pull front part with pendulum motion, remove front cover, numbers and at the picture. If there is necessary remove back part of device, please disconnect cables and unscrew two holding screws. Figure2: Device demounting IE-SNC-TX3(4)
6 Button and jumper - placing Button is placed behind small hole on the left side of the device (front view). For button pressing use thin instrument, for example paper clip. Button function is described later. Jumper is available only after the front part of device is demounted. Then look at the back side of demounted front part. Jumper is placed at the right bottom corner (at the same side as button). Jumper function is described later. Info mode If in doubt of setting of installed device, verification of its address is enabled even without using computer. Devices with RS232 interface have address always set to one. Power should be connected. Shortly press Button (jumper should be opened). Actual adjusted address of the device is displayed on LCD display at decimal base, for HWg-Poseidon s communication protocol there is shown number corresponding with ASCII address code. Next press of button exits info mode and actual measured values are displayed. Note: No measurement and communication is possible during info mode. If device stays in info mode for longer than 15 s, device automatically returns to measuring cycle. Setting of pressure correction for altitude For devices T7318 and T7418 only! If there is necessary to read value of atmospheric pressure corrected with respect to altitude, it is possible to set corresponding pressure offset for this altitude. It is possible to do it with Users software. This value is then automatically added to measured pressure value. The resultant value of pressure with added correction for altitude must be between 300 hpa and 1350 hpa (from PSI to PSI). Outside this range device sends value of Error 2! Description of communication protocols Detailed description of each communication protocols including examples of communication is available in individual document Description of communication protocols of Txxxx series which is free to download at Note: After switching ON the power of the device it can last up to 2 s before the device starts to communicate and measure! Modbus RTU Control units communicate on master-slave principle in half-duplex operation. Only master can send request and only addressed device responds. During sending of request no other slave station should respond. During communication, data transfer proceeds in binary format. Each Byte is sent as eight bit data word in format: 1 start bit, data word 8 bit (LSB first), 2 stop bits 1, without parity. Device supports communication speed from 110Bd to Bd. Sent request and response have syntax: ADDRESS OF DEVICE FUNCTION Modbus CRC 1 Device sends two stop bits, for receive one stop bit is enough. 6 IE-SNC-TX3(4)18-06
7 Supported functions 03 (0x03): Reading of 16-bit registers (Read Holding Registers) 04 (0x04): Reading of 16-bit input gates (Read Input Registers) 16 (0x10): Setting of more 16-bit registers (Write Multiple Registers) Jumper and button Jumper and button are located next to connection terminals. If communication protocol Modbus is selected the function of jumper and button is as follows: Jumper opened device memory is protected from writing, from device side it is only enabled to read measured value, writing to memory is disabled (no change of device address, communication speed and LCD setting is enabled) Jumper closed writing to device memory is enabled by means of User s software Jumper opened and button shortly pressed device goes to Info mode, see chapter Info mode Jumper closed and button pressed for longer than six seconds causes restoring of manufacturer setting of communication protocol, i.e. sets Modbus RTU communication protocol, device address sets to 01h and communication speed to 9600Bd (after button press there is def message blinking at LCD display. Six seconds later message def stays shown, it means manufacturer setting of communication protocol is done). Modbus registers of the device Variable Unit Address [hex] X Address [dec] X Format Size Status Measured temperature [ C] [ F]* 0x Int*10 BIN16 R Measured relative humidity [%] 0x Int*10 BIN16 R Computed value * [*] 0x Int*10 BIN16 R Address of device [-] 0x Int BIN16 R/W* Code of communication speed [-] 0x Int BIN16 R/W* Serial number of device Hi [-] 0x BCD BIN16 R Serial number of device Lo [-] 0x BCD BIN16 R Version of Firmware Hi [-] 0x BCD BIN16 R Version of Firmware Lo [-] 0x BCD BIN16 R Addition for devices T7310 and T with atmospheric pressure measurement Variable Atmospheric pressure Unit* hpa PSI inhg mbar oz/in 2 mmhg inh 2 O kpa Address Address [hex] X [dec] X Format Size Status Int*10 Int*1000 Int*100 0x Int*10 Int*10 BIN16 R Int*10 Int*10 Int*100 IE-SNC-TX3(4)
8 Since FW version there is possibility to read the all computed values from registers: Variable Unit Address Address [hex] X [dec] X Format Size Status Dew point temperature [ C] [ F]* 0x Int*10 BIN16 R Absolute humidity [g/m 3 ] 0x Int*10 BIN16 R Specific humidity [g/kg] 0x Int*10 BIN16 R Mixing ratio [g/kg] 0x Int*10 BIN16 R Specific enthalpy [kj/kg] 0x Int*10 BIN16 R Explanation: * depends on device setting (by User s software) Int*10 register is in format integer*10 R register is designed only for reading W* register is designed for writing, for details see file Description of communication protocols of Txxxx series X register addresses are indexed from zero register 0x31 is physically sent as value 0x30, 0x32 as 0x31 (zero based addressing). Note: In case there is a need for reading of measured values from the device with higher resolution than one decimal, measured values in device are stored also in Float format, which is not directly compatible with IEEE754. Protocol compatible with Advantech-ADAM standard Control units communicate on master-slave principle in half-duplex operation. Only master can send requests and only addressed device responds. During sending request any of slave devices should respond. During communication data is transferred in ASCII format (in characters). Each Byte is sent as two ASCII characters. Device supports communication speed from 1200Bd to Bd, parameters of communication link are 1 start bit + eight bit data word (LSB first) + 1 stop bit, without parity. Jumper Jumper is located next to connection terminals. If communication protocol compatible with standard Advantech-ADAM is selected, its function is the following: If jumper during switching ON the power is closed, device always communicates with following parameters regardless stored setting in the device: communication speed 9600 Bd, without check sum, device address 00h If jumper during switching ON the power is not closed, device communicates in accordance with stored setting. If jumper is closed during device operation, device temporarily changes its address to 00h, it will communicate in the same communication speed as before closing jumper and will communicate without check sum. After jumper is opened setting of address and check sum is reset in accordance with values stored in the device. Communication speed and check sum are possible to change only if jumper is closed. Jumper closed and button pressed for longer than six seconds causes restoring of manufacturer setting of communication protocol, i.e. sets Modbus RTU communication protocol, device address sets to 01h and communication speed to 9600Bd (after button press there is def message blinking at LCD display. Six seconds later message def stays shown, it means manufacturer setting of communication protocol is done). 8 IE-SNC-TX3(4)18-06
9 For communication with device which measure more than one value, there is necessary to add at the end of command the number of communication channel, where the measured value is mapped. Command for value reading is #AAx(CRC) cr, where AA is device address, x is number of communication channel, CRC is check sum (can be used or not). Measured value Number of communication channel Temperature 0 Relative humidity 1 Computed value 2 Atmospheric pressure 3 Command #AA(CRC) cr for reading all measured values at once is supported for multichannel devices since firmware version Response: > (temperature)(relative humidity)(dew point temperature)(absolute humidity) (specific humidity)(mixing ratio)(specific enthalpy)(atmospheric pressure)cr ARION communication protocol - AMiT company The device supports communication protocol ARiON version For more details see file Description of communication protocols of Txxxx series or Communication with HWg Poseidon units Device supports communication with HWg-Poseidon units. For communication with this unit set the device with setup software TSensor to communication protocol HWg Poseidon and set correct device address. This communication protocol supports read temperature at C, relative humidity, one of computed value (dew point temperature or absolute humidity) and barometric pressure at kpa (depended by device type). For atmospheric pressure correction to altitude setting there is Users software Tsensor. Jumper and button If communication with HWg Poseidon unit is selected, the function of jumper and button is as follows: Jumper opened and button shortly pressed device goes to Info mode, see chapter Info mode. Jumper closed and button pressed for longer than six seconds causes restoring of manufacturer setting of communication protocol, i.e. sets Modbus RTU communication protocol, device address sets to 01h and communication speed to 9600Bd - after button press there is def message blinking at LCD display. Six seconds later message def stays shown, it means manufacturer setting of communication protocol is done. IE-SNC-TX3(4)
10 Error States of the device Device continuously checks its state during operation. In case error is found LCD displays corresponding error code: Error 0 First line displays Err0. Check sum error of stored setting inside device s memory. This error appears if incorrect writing procedure to device s memory occurred or if damage of calibration data appeared. At this state device does not measure and calculate values. It is a serious error, contact distributor of the device to fix. Error 1 Measured or calculated value except in pressure is over upper limit of allowed full scale range. There is a reading Err1 on LCD display. Value read from the device is (for pressure reading there is hpa correct value) This state appears in case of: Measured temperature is higher than approximately 600 C (i.e. high non-measurable resistance of temperature sensor, probably opened circuit). Relative humidity is higher than 100%, i.e. damaged humidity sensor, or humidity calculation of humidity is not possible (due to error during temperature measurement) Computed value calculation of the value is not possible (error during measurement of temperature or relative humidity or value is over range) Error 2 There is a reading Err2 on LCD display. Measured or calculated value is below lower limit of allowed full scale range. Value read from the device is This state appears in case of: Measured temperature is lower than approximately -210 C (i.e. low resistance of temperature sensor, probably short circuit). Relative humidity is lower than 0%, i.e. damaged sensor for measurement of relative humidity, or calculation of humidity is not possible (due to error during temperature measurement) Measured pressure value with added correction for altitude is outside of range from 300 hpa to 1350 hpa (from PSI to PSI) or the pressure sensor is damaged. Please check setting of pressure correction for altitude with User s software. Computed value calculation of computed value is not possible (error during measurement of temperature or relative humidity) Error 3 There is a reading Err3 on LCD display upper line. Error of internal A/D converter appeared (converter does not respond, probably damage of A/D converter). This error does NOT affect pressure measurement. Rest values are NOT measured. It is a serious error, contact distributor of the device. Error 4 There is a reading Err4 on LCD display. It is internal device error during pressure sensor initialization. Under this condition device does NOT measure atmospheric pressure. Value read from device is Pressure sensor is probably damaged. It is a serious error, contact distributor of the device. 10 IE-SNC-TX3(4)18-06
11 Readings on LCD display C, F Reading next to this symbol is measured temperature or error state of value. %RH Reading next to this symbol is measured relative humidity or error state of value. hpa, PSI, inhg, Reading next to this symbol is measured pressure or error state of value. If selected pressure unit is mbar or oz/in 2 or mmhg or inh 2 O or kpa, there is shown only value (number) without corresponding pressure unit! C / F DP Reading next to this symbol is calculated dew point temperature or error state of value. g/m 3 Reading next to this symbol is calculated absolute humidity or error state of value. g/kg Reading next to this symbol is calculated specific humidity or mixing ratio (depends on device setting) or error state of value. If specific enthalpy is selected, there is shown only value (number) without corresponding unit! symbol 3 near by left display margin Is on if jumper is closed. Technical parameters of the device: RS 485 Interface: Receiver-Input Resistance: Devices on bus: 96 kω max. 256 (1/8 Unit Receiver Load) Measuring parameters: Ambient temperature (RTD sensor Pt1000/3850ppm): Measuring range: -10 to +50 C Resolution of display: 0.1 C Accuracy: ± 0.5 C Relative humidity - T3318, T3418, T7318 and T7418 devices only (reading is temperature compensated at entire temperature range): Measuring range: 5 to 95 %RH (see Device installation) Resolution of display: 0.1 %RH Accuracy: ± 2.5 %RH from 5 to 60 %RH, ± 3 %RH from 60 to 95 %RH, at 23 C IE-SNC-TX3(4)
12 Atmospheric pressure (T7318, T7418 only): Unit hpa, mbar PSI mmhg inhg inh 2 O oz/in 2 kpa Range Display resolution Measurement accuracy T=23 C ±1.3 ±0.02 ±1.0 ±0.04 ±0.5 ±0.3 ± T 40 C ±1.5 ±0.02 ±1.1 ±0.04 ±0.6 ±0.3 ±0.15 Else ±2.0 ±0.03 ±1.5 ±0.06 ±0.8 ±0.5 ±0.20 The value computed from ambient temperature and relative humidity (T3318, T3418, T7318 and T7418 devices only): Display resolution: 0.1 C You can choice one of the next value: Dew point temperature Range: -60 to +80 C (-76 to 176 F) Accuracy: ±1.5 C (±2,7 F) at ambient temperature T < 25 C (77 F) and relative humidity RH >30%, for more details see graphs below 12 IE-SNC-TX3(4)18-06
13 Absolute humidity Range: 0 to 400 g/m 3 Accuracy: ±1,5g/m 3 at air temperature T < 25 C (104 F), for more details see graphs below Specific humidity 2 Accuracy: Range: Mixing ratio 2 Accuracy: Range: ±2g/kg at air temperature T < 35 C (95 F) 0 to 550 g/kg ±2g/kg at air temperature T < 35 C (95 F) 0 to 995 g/kg Specific enthalpy 2 Accuracy: ± 3kJ/kg at air temperature T < 25 C (77 F) Range: 0 to 995 kj/kg 3 The values computed from ambient temperature and relative humidity including their accuracy you can exactly determine by the program Conversions. It is free to download at Response time: temperature: air flow approximately 0.3 m/s t90 < 12 min No air flow t90 < 25 min relative humidity: t90 < 30 s (air flow approximately 1 m/s, relative humidity step 65 %RH, constant temperature) atmospheric pressure 4 : t90 <44 s Recommended calibration interval: T0318, T0418: 2 years Rest types: 1 year 2 This value depends on the barometric pressure. If device doesn t support pressure measurement, then constant value stored inside device memory is used. Default value preset by manufacturer is 1013hPa and can be changed by user s software. 3 This maximum is reached under conditions about 70 C/100%RH or 80 C/70%RH 4 There is possible to change response time. For more details see file Description of calibration and adjustment procedure.pdf, which is installed together with Users software.. IE-SNC-TX3(4)
14 Measuring interval and LCD display refresh: 0.5 s, atmospheric pressure 2 s Power: 9 to 30 V dc Consumption: T0318, T3318, T7318 (RS232) 6mA T0418, T3418, T7418 (RS485) max 0.5 W Protection: IP20 Operating conditions: Operating temperature range: -10 to +50 C Operating humidity range: 0 to 100 %RH (without condensation) Outer characteristics in accordance with Czech National Standart , normal environment with the specifications: AE1, AN1, BE1 Electromagnetic compatibility: complies EN Storing conditions: temperature -30 to +80 C, humidity 0 to 100 %RH without condensation Not allowed manipulations: It is not allowed to operate the device under other than specified conditions in technical parameters. Devices are not designed for locations with chemically aggressive environment. Temperature and humidity sensors must not be exposed to direct contact to water or other liquids. Do not use the device in an explosive environment. Dimensions: 106 x 88 x 33 (h x l x d) Weight: approximately 150 g Material of the case: ABS End of operation Device itself (after its life) is necessary to liquidate ecologically! Technical support and service Technical support and service is provided by distributor. For contact see warranty certificate. 14 IE-SNC-TX3(4)18-06
15 Appendix A Connection of transmitters with RS485 output to the PC The ELO E214 converter is an optional accessory for connection of transmitter with RS485 interface to the PC via USB port. Link RS485 is connected across pin 9 A(+) and pin 8 B(-). The pull up, pull down and termination resistors are part of the transmitter. These internal resistors can be connected to the bus by connecting the corresponding pins of CANON connector (for more information see the operation manual for ELO E214). The ELO E06D converter is an optional accessory for connection of transmitter with RS485 interface to the PC via serial port RS232. Connector marked RS232 connect directly to the PC. Power voltage +6V DC from an external acdc adapter connect to pin 9 of connector marked RS485, 0V connect to pin 5 and link RS485 connect across pin 3 A(+) and pin 4 B(-). Time out setting is performed by connecting the corresponding pins of connector marked RS485 (for more information see the operation manual for ELO E06D). IE-SNC-TX3(4)
T2314, T2414. Instruction Manual
Atmospheric pressure transmitter T2314, T2414 with RS232 / RS485 serial output Instruction Manual Instruction Manual Device type Pressure Output Galvanic isolated output T2314 RS232 - T2414 RS485 Device
More informationT2314, T2414. Instruction Manual
Atmospheric pressure transmitter T2314, T2414 with RS232 / RS485 serial output Instruction Manual Instruction Manual Device type Pressure Output Galvanic isolated output T2314 RS232 - T2414 RS485 Device
More informationT3311, T3313, T3411 T7310, T7410. Instruction Manual
Programmable transmitter of temperature, relative humidity and other derived humidity values T3311, T3313, T3411 Programmable transmitter of atmospheric pressure, temperature, relative humidity and other
More informationProgrammable transmitter of temperature, relative humidity and other derived humidity values with RS485 serial output Instruction Manual
TRANSMITTER T3413, T3417 Programmable transmitter of temperature, relative humidity and other derived humidity values with RS485 serial output Instruction Manual Instruction Manual for use of temperature
More informationTRANSDUCER T4311, T4411
TRANSDUCER T4311, T4411 Programmable temperature transducer for RTD Pt1000 sensor with serial output RS232 and RS485 Instruction manual Instruction Manual for use of transducer: T4311 (RS232), T4411 (RS485)
More informationT3319, T3419 T7311, T7411. Instruction Manual
Programmable transmitter of temperature, relative humidity and other derived humidity values T3319, T3419 Programmable transmitter of atmospheric pressure, temperature, relative humidity and other derived
More informationAT-VLI-102DRS. Manual. ATAL B.V. Ampèrestraat NL-1446 TR PURMEREND. Postbus 783 NL-1440 AT PURMEREND T (+31) F (+31)
AT-VLI-102DRS Manual ATAL B.V. Ampèrestraat 35-37 NL-1446 TR PURMEREND Postbus 783 NL-1440 AT PURMEREND T (+31) 0299 630 610 F (+31) 0299 630 611. E info@atal.nl I www.atal.nl Instruction Manual The transmitters
More informationProgrammable transmitter of temperature, relative humidity and other derived humidity values with 0 to 10 V outputs Instruction Manual
T0210 TRANSMITTER Programmable transmitter of temperature, relative humidity and other derived humidity values with 0 to 10 V outputs Instruction Manual Instruction manual for use of T0210 transmitter
More informationT2214. Instruction Manual
Programmable atmospheric pressure transmitter T2214 with 0 to 10 V output Instruction Manual Instruction manual for use of T2214 device Device is designed for measurement of atmospheric pressure at hpa,
More informationTemperature, humidity and pressure regulator. with RS485 serial output H0430 H3430 H3431 H3433 H3437 H4431 H7430 H7431. Instruction Manual
Temperature, humidity and pressure regulator with RS485 serial output H0430 H3430 H3431 H3433 H3437 H4431 H7430 H7431 Instruction Manual 1. GENERAL SAFETY RULES...3 2. GENERAL DESCRIPTION...4 3. REGULATOR
More informationTRANSMITTER T3311, T3411
TRANSMITTER T3311, T3411 Programmable relative humidity and temperature transmitter with serial output RS232 and RS485 With computing of dew point temperature, absolute humidity, specific humidity, mixing
More informationProgrammable temperature transducer from Pt1000 sensor to current loop 4-20 ma Instruction Manual
T4111 TRANSDUCER Programmable temperature transducer from Pt1000 sensor to current loop 4-20 ma Instruction Manual Instruction manual for use of T4111 transducer Transducer is designed for temperature
More informationTemperature, humidity and pressure regulator. with RS485 serial output H0430 H3430 H3431 H3433 H3437 H4431 H7430 H7431. Instruction Manual
Temperature, humidity and pressure regulator with RS485 serial output H0430 H3430 H3431 H3433 H3437 H4431 H7430 H7431 Instruction Manual Table of content 1. GENERAL DESCRIPTION... 5 2. REGULATOR MOUNTING
More informationDescription of communication protocols of Txxxx series
Description of communication protocols of Txxxx series DESCRIPTION OF COMMUNICATION PROTOCOLS... 3 MODBUS RTU... 3 Supported functions... 3 Jumper and button... 3 Description of supported function... 4
More informationInstruction Manual. T3110 T3110L T3110Ex
www.cometsystem.cz Instruction Manual T3110 T3110L T3110Ex Programmable transmitter of temperature, relative humidity and other calculated humidity values with 4-20 ma outputs Copyright: COMET System,
More informationTemperature and humidity regulator H3020 H3021 H3023 H3027. Instruction Manual
Temperature and humidity regulator H3020 H3021 H3023 H3027 Instruction Manual Table of content 1. GENERAL SAFETY RULES... 3 2. GENERAL DESCRIPTION... 4 3. REGULATOR MOUNTING AND CONNECTION... 4 4. DESCRIPTION
More informationCommunication protocols description of. Hx4xx and Hx3xx regulators with RS485 and RS232 communication interface
Communication protocols description of Hx4xx and Hx3xx regulators with RS485 and RS232 communication interface Copyright: COMET System, Ltd. It is prohibited to copy and edit this manual and make any changes
More informationRack mount environment monitor
Rack mount environment monitor H3531R H4531R H7531R Monitoring of temperature, humidity, barometric pressure and other derived humidity values with Ethernet interface Instruction Manual Table of content
More informationT5540. Programmable transmitter of temperature, relative humidity, CO 2 and other derived humidity values with Ethernet connection T6540
CO 2 concentration transmitter with Ethernet connection T5540 Programmable transmitter of temperature, relative humidity, CO 2 and other derived humidity values with Ethernet connection T6540 Instruction
More informationDual channel temperature logger with two voltage inputs 0-5V Instruction Manual
LOGGER S0541 Dual channel temperature logger with two voltage inputs 0-5V Instruction Manual Instruction Manual for use of S0541 logger Instrument is designed for measurement and record of temperature
More informationsensor, which compensates for ageing effects, is highly insensitive to pollution and offers outstanding long term stability.
USER S GUIDE EE800 - HVAC Room Transmitter for CO 2, Temperature and Relative Humidity GENERAL EE800 combines CO 2, temperature (T) and relative humidity (RH) measurement in one device with modern design.
More informationDual channel temperature logger with display Instruction Manual
LOGGER S0122 Dual channel temperature logger with display Instruction Manual ie-log-s0122-05 Instruction manual for use of temperature logger S0122 Logger is designed for measurement and record of ambient
More informationAT-VLS-104DE. Manual. ATAL B.V. Ampèrestraat NL-1446 TR PURMEREND. Postbus 783 NL-1440 AT PURMEREND T (+31) F (+31)
AT-VLS-104DE Manual ATAL B.V. Ampèrestraat 35-37 NL-1446 TR PURMEREND Postbus 783 NL-1440 AT PURMEREND T (+31) 0299 630 610 F (+31) 0299 630 611 E info@atal.nl I www.atal.nl Inhoud Manual... 1 1. General
More informationTemperature logger with internal sensor Instruction manual
LOGGER R0110 Temperature logger with internal sensor Instruction manual Manual for use of temperature logger R0110 Logger is designed for measurement and record of temperature from built-in internal temperature
More informationTemperature logger with display Instruction Manual
LOGGER S0110 Temperature logger with display Instruction Manual Instruction manual for use of temperature logger S0110 Logger is designed for measurement and record of temperature from built-in internal
More informationIntelligent pressure meter with Ethernet connection T2514
Intelligent pressure meter with Ethernet connection T2514 Intelligent temperature, relative humidity meter with Ethernet connection With calculation of dew point temperature, absolute humidity, specific
More informationDual channel temperature logger with two binary inputs and LCD display Instruction Manual
LOGGER S0841 Dual channel temperature logger with two binary inputs and LCD display Instruction Manual Instruction Manual for use of S0841 logger Instrument is designed for measurement and record of temperature
More informationRST ROOM TEMPERATURE TRANSMITTER. Mounting and operating instructions
Mounting and operating instructions Table of contents SAFETY AND PRECAUTIONS 3 PRODUCT DESCRIPTION 4 ARTICLE CODES 4 INTENDED AREA OF USE 4 TECHNICAL DATA 4 STANDARDS 4 OPERATIONAL DIAGRAM 5 WIRING AND
More informationGREISINGER electronic GmbH D Regenstauf, Hans-Sachs-Straße 26
H20.0.24.6C1-07 EASYBus-Sensor module for humidity temperature with option: selectable humidity display from version V3.2 Operating Manual EBHT 2R / UNI Content 1 INTENDED USE 2 2 GENERAL ADVICE 2 3 SAFETY
More informationHPS-M -2 DIFFERENTIAL PRESSURE TRANSMITTER. Mounting and operating instructions
DIFFERENTIAL PRESSURE Mounting and operating instructions Table of contents SAFETY AND PRECAUTIONS 3 PRODUCT DESCRIPTION 4 ARTICLE CODES 4 INTENDED AREA OF USE 4 TECHNICAL DATA 4 STANDARDS 5 OPERATIONAL
More informationwith serial RS485/RS232 output
with serial RS485/RS232 output RS485 programmable sensors of temperature, humidity, atmospheric pressure and CO 2 with two-state inputs and relay outputs industry and interior design high quality, accurate
More informationTEMPERATURE AND HUMIDITY TRANSDUCER P18 TYPE USER S MANUAL
TEMPERATURE AND HUMIDITY TRANSDUCER P18 TYPE USER S MANUAL 1 2 CONTENTS 1. APPLICATION... 5 2. BASIC REQUIREMENTS, OPERATIONAL SAFETY... 5 3. INSTALLATION... 5 3.1. Assembly...5 3.2. Electrical Connections...7
More informationwith serial RS485/RS232 output
with serial RS485/RS232 output RS485 programmable sensors of temperature, humidity, atmospheric pressure and CO 2 with two-state inputs and relay outputs industry and interior design high quality, accurate
More informationDXTH DUCT SENSOR / SWITCH FOR TEMPERATURE AND HUMIDITY. Mounting and operating instructions
DUAL DUCT SENSOR / SWITCH FOR TEMPERATURE AND HUMIDITY Mounting and operating instructions Table of contents SAFETY AND PRECAUTIONS 3 PRODUCT DESCRIPTION 4 ARTICLE CODES 4 INTENDED AREA OF USE 4 TECHNICAL
More informationRXTH DUAL ROOM SENSOR / SWITCH
DUAL ROOM SENSOR / SWITCH FOR TEMPERATURE AND RELATIVE HUMIDITY Mounting and operating instructions Table of contents SAFETY AND PRECAUTIONS 3 PRODUCT DESCRIPTION 4 ARTICLE CODES 4 INTENDED AREA OF USE
More informationModbus Manual Version Modbus Manual for Clean Room Panel CRP5
Page 1 of 42 Modbus Manual Version 1.03 Modbus Manual for Clean Room Panel CRP5 This manual is for persons who will use the Clean Room Panel Modbus protocol. It describes how messages are constructed and
More informationPTU300 Combined Pressure, Humidity and Temperature Transmitter
PTU300 Combined Pressure, Humidity and Temperature Transmitter For Demanding Applications Features Barometric pressure, humidity, and temperature measurement in one transmitter RS-232C serial interface
More informationRXTP ROOM TEMPERATURE
ROOM TEMPERATURE CONTROLLER WITH PI CONTROL Mounting and operating instructions Table of contents SAFETY AND PRECAUTIONS 3 PRODUCT DESCRIPTION 4 ARTICLE CODES 4 INTENDED AREA OF USE 4 TECHNICAL DATA 4
More informationUSER S GUIDE. EE210 - Humidity and Temperature Transmitter for demanding Climate Control Applications GENERAL
USER S GUIDE EE210 - Humidity and Temperature Transmitter for demanding Climate Control Applications GENERAL The EE210 transmitter, available for wall or duct mounting, is designed for the highly accurate
More informationTCNM-ACBB1 Installation Manual
The TCNM-ACBB1 is a connection box that can be used as an accessory to facilitate system connections for installation and device replacement of several Banner family reading devices. System cabling is
More informationMU110-6U. Analog output module 6 channel. User guide
MU110-6U Analog output module 6 channel User guide MU110-6U_2016.12_0221_EN All rights reserved Subject to technical changes and misprints akytec GmbH Vahrenwalder Str. 269 A 30179 Hannover Тел.: +49 (0)
More informationHARDENED ROOM SENSOR USER MANUAL SAD120 CPO55 E 1
HARDENED ROOM SENSOR USER MANUAL SAD120 CPO55 LOREME 12, rue des Potiers d'etain Actipole BORNY - B.P. 35014-57071 METZ CEDEX 3 Phone 03.87.76.32.51 Contact : Commercial@Loreme.fr - Technique@Loreme.fr
More informationDSTHM-2 COMBINED T AND RH DUCT TRANSMITTER. Mounting and operating instructions
Mounting and operating instructions Table of contents SAFETY AND PRECAUTIONS 3 PRODUCT DESCRIPTION 4 ARTICLE CODES 4 INTENDED AREA OF USE 4 TECHNICAL DATA 4 STANDARDS 4 OPERATIONAL DIAGRAMS 5 WIRING AND
More informationABB Drives. User s Manual. Modbus Adapter Module RMBA-01
ABB Drives User s Manual Modbus Adapter Module RMBA-01 Modbus Adapter Module RMBA-01 User s Manual 3AFE 64498851 REV A EN EFFECTIVE: 1.3.2002 2002 ABB Oy. All Rights Reserved. Safety instructions Overview
More informationHygroClip DI Digital Interface for HygroClip Probes v 1.0 Instruction Manual
HygroClip DI Digital Interface for HygroClip Probes v 1.0 Instruction Manual page 2 of 15 Contents: Overview... 2 Models... 3 Power... 4 Probes... 4 Connector identification... 5 Pin-out diagrams... 6
More informationSDM-8AO. Expansion Module 8 analog outputs. Manufactured for
Version 1.0 16.05.2014 Manufactured for Thank you for choosing our product. This manual will help you with proper support and proper operation of the device. The information contained in this manual have
More informationSDM-6RO. Expansion Module 6 relay outputs. Manufactured for
Version 1.0 5.02.2014 Manufactured for Thank you for choosing our product. This manual will help you with proper support and proper operation of the device. The information contained in this manual have
More informationTEMPERATURE AND HUMIDITY TRANSDUCER P18(D) TYPE
TEMPERATURE AND HUMIDITY TRANSDUCER P18(D) TYPE user s manual 1 Contents 1. Application... 5 2. Transducer set... 7 3. Basic requirements, operational safety... 7 4. Installation... 7 4.1. Way of fixing...
More informationEE211. Humidity and Temperature Transmitter for Continuous High Humidity. Features. 42 v1.3 / Modification rights reserved EE211 EE211
Humidity and Temperature Transmitter for Continuous High Humidity The is dedicated for accurate and long term stable measurement under continuous high humidity (>85 % RH) and condensing conditions in demanding
More information3-step setting 2. 2-Color Display High-Precision Digital Pressure Switch. ZSE30A(F)/ISE30A Series. Added vacuum range.
2-Color Display High-Precision Digital Pressure Switch ZSE3A(F)/E3A Series RoHS Can copy to up to 1 switches simultaneously. setting labor Minimizing ZSE3 E3 ZSE4 E4 The settings of the master sensor can
More informationP3-SCM. General Specifications
General Specifications Module Type Modules per Base Modules per Group I/O Points Used Field Wiring Connector Operating Temperature Storage Temperature Humidity Environmental Air Vibration Shock Field to
More informationMPI-DN, MPI-D MULTICHANNEL ELECTRONIC RECORDER for HART or RS-485/ MODBUS RTU SENSORS
MPI-DN, MPI-D MULTICHANNEL ELECTRONIC RECORDER for HART or RS-485/ MODBUS RTU SENSORS 18 channels for HART / Modbus RTU sensors 2 digital channels 16 math channels 4 relay outputs for alarm or control
More informationSeries Pressure Sensor Instruction Sheet
2018/05/10 Series ure Sensor Instruction Sheet Thank you very much for choosing Delta DPA series pressure sensor. Please read this instruction sheet carefully before using your DPA. Keep this instruction
More informationDigital thermo-hygro-barometer with external probe Manual for use
COMMETER D4141 Digital thermo-hygro-barometer with external probe Manual for use Instruction manual for use of thermo-hygro-barometer COMMETER D4141 Instrument is designed for measurement and data logging
More informationUSER GIDE COMET SYSTEM
COMET SYSTEM www.cometsystem.com Web Sensor T0510 Web Sensor T4511 Web Sensor T3510 Web Sensor T3511 Web Sensor T3511P Web Sensor T7510 Web Sensor T7511 Web Sensor T2514 USER GIDE Copyright: COMET System,
More informationHD B. [ GB ] Precision Barometer
HD 9408.3B [ GB ] Precision Barometer [ GB ] [ GB ] Characteristics High accuracy temperature-compensated sensor with excellent stability Wide temperature operating range Various output options available
More informationRS-FS-N01 Wind speed transmitter user's Guide (485type)
RS-FS-N01 Wind speed transmitter user's Guide (485type) Issue: V1.0 1 2 Context 1. Introduction... 4 2. Installation instructions...5 3. Configure the software installation and use... 6 4. Communication
More informationisma-b-fcu FCU Hardware User Manual Global Control 5 Sp. z o.o. Warsaw, Poland
isma-b-fcu User Manual FCU Hardware Global Control 5 Sp. z o.o. Warsaw, Poland www.gc5.pl Table of contents 1 Introduction 3 1.1 Document change log 3 1.2 Safety rules 3 1.3 Technical specifications 4
More informationTSA TEMPERATURE SWITCHES 15.13a
TSA TEMPERATURE SWITCHES 15.13a DESCRIPTION AND APPLICATION These temperature switches are designed for using as two-state controllers (ON/OFF type control). They compare the temperature set-point with
More informationDCC-8 DIGITAL TO EIGHT CURRENT LOOP CONVERTER OPERATING MANUAL
DCC-8 DIGITAL TO EIGHT CURRENT LOOP CONVERTER OPERATING MANUAL 1 TABLE OF CONTENTS 1. MOUNTING INSTRUCTIONS 1.1 Standard DIN Rail mounting 1.2 Screw Mounting 2. FUSE REPLACEMENT 3. ASSEMBLING THE UNIT
More informationTable of Contents. General Information. Document Sure-Aire Flow Monitoring System. User and Service Manual WARNING CAUTION
Document 476092 User and Service Manual Installation, Operation and Maintenance Manual Please read and save these instructions for future reference. Read carefully before attempting to assemble, install,
More informationCarbon Monoxide Sensor - ModBus
Introduction The CO Sensor uses an electrochemical sensor to monitor CO level in a range of 0 to 500 ppm and communicates via an RS-485 network configured for ModBus protocol. Before Installation Read
More informationFEATURES DESCRIPTION FEATURES
FEATURES Two High Speed Counters Two Pulse Train Outputs Two Pulse Width Modulation Outputs 24 Sinking or Sourcing Inputs 16 Outputs 1 RS232 Port 2 RS485 Ports Supports Modbus RTU Protocol Communicate
More informationR1M-GH THERMOCOUPLE & DC INPUT MODULE MODEL. Remote I/O R1M Series. (16 points)
Remote I/O R1M Series THERMOCOUPLE & DC INPUT MODULE (16 points) MODEL MODEL & SUFFIX CODE SELECTION R1MGH2T MODEL Modbus protocol I/O TYPE GH2 : Thermocouple or DC input, 16 points FIELD TERMINAL TYPE
More informationGFK-2415A March Type of sensor connection
VersaMax IP Expansion Module has four analog differential inputs that can be configured as current or voltage inputs. It connects to a local bus that is interfaced to a Profibus-DP / PROFINET network by
More information1/32-DIN TEMPERATURE CONTROLLER INSTALLATION, WIRING AND OPERATION MANUAL FORM 3882
1/32-DIN TEMPERATURE CONTROLLER INSTALLATION, WIRING AND OPERATION MANUAL FORM 3882 This manual is intended for use in support of installation, commissioning and configuration of the 1/32-DIN Temperature
More informationRS-FX-N01 wind transmitter user's Guide (485type)
RS-FX-N01 wind transmitter user's Guide (485type) Issue:. V1. 0 1 2 Context 1. Introduction...4 2. Installation instructions... 5 3. Configure the software installation and use...7 4. Communication Protocol...
More informationTango. alpha nea. Thermometers and controllers with digital communication - Series AM
Installed in Tango (standard) or alpha nea frames Modbus RTU communication over RS485 line Wide range of power supply Control knob for correction setting Can be installed in a multifunction frame Tango
More informationMODBUS RTU I/O Expansion Modules - Models C267, C277, and C287. Installation and Operations Manual Section 50
MODBUS RTU I/O Expansion Modules - Models C267, C277, and C287 Installation and Operations Manual 00-02-0651 09-01-09 Section 50 In order to consistently bring you the highest quality, full featured products,
More informationUSER GUIDE COMET SYSTEM
COMET SYSTEM www.cometsystem.cz Web Sensor T0510 Web Sensor T4511 Web Sensor T3510 Web Sensor T3511 Web Sensor T3511P Web Sensor T7510 Web Sensor T7511 Web Sensor T2524 USER GUIDE Copyright: COMET System,
More informationGeneral Specifications. P2-SCM Serial Communications
General Specifications Module Type Intelligent Modules per Base I/O Points Used Field Wiring Connector Operating Temperature Storage Temperature Humidity Environmental Air Vibration Shock Field to Logic
More informationEE310. High-End Humidity and Temperature Transmitter for Demanding Process Control. Typical applications. Features EE310 EE310
is optimized for reliable measurement in demanding industrial applications. In addition to highly accurate measurement of relative humidity (RH) and temperature (T), the transmitter also calculates parameters
More informationGMM220 CO 2. Transmitter Modules. Introduction. Mounting
Introduction GMM220 CO 2 Transmitter Modules Vaisala GMM220 transmitter modules are versatile instruments for measuring CO 2 in industrial applications. The CARBOCAP sensor is silicon based and its operation
More informationMXPLC. Compact PLC process station. Summary. Application HVAC control systems, data acquisition, interfacing 3 rd party systems.
MXPLC Compact PLC process station Summary The MXPLC is a programmable process station with integrated I/O module with the I/O mix optimized for larger HVAC control applications. The multi-interface process
More informationTOXALERT MODEL AIR 2000
TOXALERT MODEL AIR 2000 NOTE: Toxalert s Model GVU-CO 2 Sensor is the same as the Air2000R. Microprocessor-based, Infrared Environmental CO 2 Sensor OPERATOR S MANUAL TOXALERT TM INTERNATIONAL INC. P.O.
More informationMXIO. Compact I/O module. Summary. Application Compact I/O module for data acquisition and HVAC control systems. Function
MXIO Compact I/O module Summary The MXIO multiple I/O compact module is a microprocessor-controlled, communicative module with the I/O mix optimized for larger HVAC control applications. The module uses
More informationTransmitters RHT-WM-485-LCD, RHT-DM-485-LCD and RHT-P LCD
Transmitters RHT-WM-485-LCD, RHT-DM-485-LCD and RHT-P10-485-LCD TEMPERATURE AND HUMIDITY TRANSMITTER INSTRUCTIONS MANUAL V1.0x D 1 INTRODUCTION The RHT-WM-485-LCD, RHT-DM-485-LCD and RHT-P10-485-LCD transmitters
More informationOutput signal. 22DTM-16 BACnet DC V, DC V. Electrical data Power supply DC V, ±10%, 0.3 W
Duct Sensor CO₂ / Humidity / Temperature For combined measurement of CO₂, relative humidity and temperature in the duct. Dual channel CO₂ technology. The measured values are output via BACnet. NEMA 4X
More informationMulti Units Humidity/Temperature Transmitter. HygroViewer Model JW300 User Manual
Multi Units Humidity/Temperature Transmitter HygroViewer Model JW300 User Manual 1. Electrical Wired & Installation The power cord is a one-meter length, 22 AWG, 7 different colors for recognition. Please
More informationTRAINING GUIDE LEVEL 3 MODBUS WRITE IMPORT COMMAND
OleumTechTM TRAINING GUIDE LEVEL 3 MODBUS WRITE IMPORT COMMAND MUST BE FAMILIAR WITH LEVEL 1 TRAINING MATERIALS BEFORE MOVING FORWARD Doc ID# 80-6010-001b TABLE OF CONTENTS 1. WHAT IS NEW WRITE IMPORT
More informationList of Contents 1. INTRODUCTION DEFINITIONS AND ABBREVIATIONS REFERENCES TECHNICAL DATA GENERAL MODBUS RTU...
MAGX2 RTU User Guide -0- V1.5 23-01-2018 List of Contents 1. INTRODUCTION... 2 1.1 DEFINITIONS AND ABBREVIATIONS... 2 1.2 REFERENCES... 2 2. TECHNICAL DATA... 3 2.1 GENERAL MODBUS RTU... 4 3. COMMISSIONING...
More informationRS485 MODBUS Module 8AO
Version 1.3 12/02/2013 Manufactured for Thank you for choosing our product. This manual will help you with proper support and proper operation of the device. The information contained in this manual have
More informationHydrostatic filling level sensor HFB C4 / R / MD
Hydrostatic filling level sensor HFB C4 / R / MD Pressure measuring range 0-0.5 bar Voltage supply 18 30 V DC Features Filling level detection through measuring the hydrostatic medium pressure by means
More informationMGate 5111 Quick Installation Guide
MGate 5111 Quick Installation Guide Edition 1.0, December 2017 Technical Support Contact Information www.moxa.com/support Moxa Americas: Toll-free: 1-888-669-2872 Tel: 1-714-528-6777 Fax: 1-714-528-6778
More informationRAD-DI8-IFS. I/O extension module with 8 digital inputs or 2 pulse inputs. INTERFACE Data sheet. 1 Description
I/O extension module with 8 digital inputs or 2 pulse inputs INTERFACE Data sheet 0483_en_00 PHOENIX CONTACT 203-04-05 Description The I/O extension module can be used in conjunction with Radioline wireless
More informationIFC 100 Supplementary instructions
IFC 100 Supplementary instructions Signal converter for electromagnetic flowmeters Description of Modbus interface Electronic Revision: ER 3.0.xx Modbus version: 1.0.xx KROHNE CONTENTS IFC 100 1 Important
More informationRS485 MODBUS Module 6RO
Version 2.0 12/02/2013 Manufactured for Thank you for choosing our product. This manual will help you with proper support and proper operation of the device. The information contained in this manual have
More informationRAD-DO8-IFS. I/O extension module, eight digital transistor outputs. Data sheet. 1 Description
I/O extension module, eight digital transistor outputs Data sheet 105364_en_00 PHOENIX CONTACT 2013-03-26 1 Description The I/O extension module can be used in conjunction with Radioline wireless modules
More informationModbus communication module for TCX2: AEX-MOD
Modbus communication module for TCX2: Communication Specification Features S485 2-wire MODBUS standard in accordance with EIA/TIA 485. Slave type of communication Supports up to 127 nodes on one network
More informationModbus Manual Version Modbus Manual for PF4/5
Modbus Manual Version 1.1 - Modbus Manual for PF4/5 Seite 2 1. Table of contents 1 Modbus protocol... 3 1.1. Structure of the Modbus protocol... 3 1.1.1 Modbus RTU / TCP... 3 1.2 Modbus Data Format...
More informationMGate 5105-MB-EIP Quick Installation Guide
MGate 5105-MB-EIP Quick Installation Guide Edition 2.2, March 2019 Technical Support Contact Information www.moxa.com/support Moxa Americas: Toll-free: 1-888-669-2872 Tel: 1-714-528-6777 Fax: 1-714-528-6778
More informationUC102 basic version with display and knob UC102BL version with display, knob and backlight UC102DK version without knob and display
UC102 Communicative heating controller Summary UC102 is a communicative room heating controller with two inputs and one PWM output for control of a radiator or electrical heater. It can work autonomously,
More informationHygroFlex HF3 Transmitters. User Guide
Page 1 of 27 HygroFlex HF3 Transmitters User Guide Page 2 of 27 Table of contents 1 Overview... 3 2 Mechanical configurations and dimensions... 4 2.1 Display option... 5 3 General description... 6 3.1
More informationUSER GUIDE COMET SYSTEM
COMET SYSTEM www.cometsystem.com Web Sensor T0610 with PoE Web Sensor T4611 with PoE Web Sensor T3610 with PoE Web Sensor T3611 with PoE Web Sensor T7610 with PoE Web Sensor T7611 with PoE Web Sensor T7613D
More informationinstallation Operation ADDRESS product diagram H8030/8031 INSTALLATION GUIDE
POWER MONITORING INSTALLATION GUIDE H8030/8031 H8030/8031 Modbus Energy Meter Networked kw/kwh Transducer Product Identification Model Max Amps CT Size Enhanced Data Stream Meters H8030-0100- 100 H8030-0300-
More informationMS Protocol Converter. User Manual. Firmware version 2.0 ISI. Instrumental Solutions, Inc.
MS1-2150 Protocol Converter User Manual Firmware version 2.0 ISI Instrumental Solutions, Inc. WWW.ISIDEV.NET Introduction The MS1-2150 protocol converter can take readings from 1 or more ModBus registers
More informationReal Time Clock with Temperature Sensor and RS485/Modbus Comunications
Real Time Clock with Temperature Sensor and RS485/Modbus Comunications April 29, 2014 Power 8 20 VDC @ less than 100 MA. Battery connect jumper RS485 Bus Load Jumpers Model: RTC-TI2C Page 1 of 6 Features:
More informationMeasuring transducers MI4x0 series Programmable transducers for RTD sensors MI450
Measuring transducers MI4x0 series Programmable transducers for RTD sensors MI450 o Measuring of resistance of RTD sensors (Pt100, Pt1000, Ni100, Cu10,...) o Accuracy class up to: 0.5 o Programmable input
More information1 IF-812 or IF-815 Terminal (Slave) 2 Intended Use. 3 Assembly and Installation _V IF-812/IF-815
95-10324_V2016-11-23 IF-812/IF-815 1 IF-812 or IF-815 Terminal (Slave) Thank you for choosing an Interflex system. With an IF-812 or IF-815 terminal (slave), you have purchased a reliable device for capturing
More informationF1000 User's Manual. (Version: V1.01)
(Version: V1.01) Contents Chapter 1 Overview... 2 Chapter 2 Installation... 3 2.1 Installation guide... 3 2.1.1 Installation position... 3 2.1.2 NEMA4 standard installation... 3 2.1.3 Environment precautions...
More information